Explosion Takes Out AtariAge [Updated]


Albert

Recommended Posts

I agree with you here. I think some (esp. IT professionals) are being sympathetic, but it sounds like they were not prepared for this, and they have never said what caused the short that resulted in an explosion. Lots of questions are unanswered, such as why there wasn't a circuit breaker to prevent the explosion from a short, and if human error caused the short. If human error caused this, they should own up to that.

Yeah, I'm not sure we'll ever know exactly why this transpired, unless they get sued for this extended downtime (which is possible). I assume a thorough investigation will be done and that The Planet will know damn well what happened. But if it puts the blame on their shoulders, they'll never share that information willingly. Hell, their front page has had NO mention of this situation at all, which is very telling in my opinion.

 

..Al

Link to comment
Share on other sites

Lots of questions are unanswered, such as why there wasn't a circuit breaker to prevent the explosion from a short, and if human error caused the short. If human error caused this, they should own up to that.

 

The function of a fuse or circuit breaker is to prevent wires from overheating due to sustained overloads. In low-current applications, they may also prevent damage from short circuits, but in some higher-current applications the best one can hope for is to avoid cascading faults.

Link to comment
Share on other sites

Lots of questions are unanswered, such as why there wasn't a circuit breaker to prevent the explosion from a short, and if human error caused the short. If human error caused this, they should own up to that.

 

The function of a fuse or circuit breaker is to prevent wires from overheating due to sustained overloads. In low-current applications, they may also prevent damage from short circuits, but in some higher-current applications the best one can hope for is to avoid cascading faults.

Point taken, but there should be some sort of failsafe to prevent explosions, especailly in indoor electrical rooms.

Link to comment
Share on other sites

Too bad AtariAge can't be hosted in a couple of locations, so if one server is unavailable for any reason, the backup (exact copy) in another state can kick in. Is that even possible?

Sure, it's possible, but it would at least double the current expenses of hosting AtariAge so it's not really feasible. Unless you want to donate $400 a month to the cause. :)

I would if I could, but I bet good old uncle AdSense might be able to do it. :D

Link to comment
Share on other sites

Joe decides he'll bring his board back up by closing a bus tie out of phase. That tripped the main breakers on 5 and 7 instantly, transferring the load from 5, 7, and 8 to 1 and 4. The noises I heard were breakers tripping throughout the plant, and the AC behind me as it single phased.

 

How do big generators work? I would expect that they use coils on both the rotor and the stator (like a car's alternator). I'm curious, though: how many of what sort of windings does a typical generator have? And do they not have some sort of electronic controls to ensure that things are within 30 degrees of phase when they switch in?

 

These units had wye connected windings on the stator, and I believe the field windings were single phase of 120VAC, but it was one leg of 120VAC phase to phase, not phase to ground. The emergency generators were a little different.

The plant had some crude electronic controls. This isn't surprising, especially given the fact the plant was built in the early sixties by the lowest bidder. They've got protection for reverse power, over speed, over current, over voltage, low oil pressure in the generator, and that's all I know of. Everything else was reacted to by the operators.

 

To my knowledge, three phase wye connections are pretty common. In that case, you have three primary coils, each with many poles around the stator. In addition to that, you'll have either a three phase delta in the field, or you'll step down a single phase of the output and send that to a single field winding.

Even at 30 degrees out of phase, though, it's still going to put a strain on the generators and most likely it will trip at least one of them. We were taught to parallel 5 degrees ahead of the bus with the synchroscope spinning "slowly in the fast direction". It takes a second for the breakers to close, and during that time, the phasing would actually get closer than 5 degrees--in fact, it was usually dead accurate by the time the breakers closed.

Link to comment
Share on other sites

Glad that AA is back on-line. Hopefully this site backed-up somewhere else, in case the hosting servers and their back-ups go down for whatever reason (I'm probably just showing my ignorance on the subject). I heard about the explosion, but I didn't connect the event to the fact that I couldn't connect to the AtariAge site; I thought it was a bad connection on my side.

Link to comment
Share on other sites

N+1 means that there is one more module active than is required to maintain the system. Sun servers, for example, may need two power supplies to function so there are three supplies built into the system. If one fails, the other two hold up power and you stay up. You replace them hot.

 

Most server class machines have at least two power feeds, normally fed by independent sources all the way back to the utility companies primaries. This allows some dummy to clip off the power pole in front of your building without you going down - you're held up on the power feed at the rear of your facility. (same goes for Internet connectivity) In a High Availability configuration, this includes a battery UPS and a generator in each leg. The generator only takes about 15 seconds to come online so your batteries usually have plenty of reserve. The UPS checks its batteries periodically and the generator usually runs a 30 minute test every week.

 

It's not rocket science - we've been doing this for a long time.

 

Bob

 

 

 

What does The Planet website mean with "N+1 redundancy". Does that mean they have N+1 backup devices. Or we have just 1 backup device?

 

If it is N+1, why didn't they have a 2nd generator for the 1st floor?

Link to comment
Share on other sites

Albert...what about buying or putting together your own server (for AA) that way if this incident happens again, you've got a back up

 

doesn't need to be a 'super duper' server...just something that fits the purpose (and it will solve your 'alternative hosting' options)

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...